Duck Butter 07-25-2011 02:59 PM

Electrical Question
 
2 Attachment(s)
Need help converting to a 200 amp meterbase. i just need to switch the wires:eek: Someone :help:

Can you match the old (letters) to the new (numbers) on the 200 amp meterbase

Duck Butter 07-25-2011 03:02 PM

2 Attachment(s)
here are some close up pics

eman 07-25-2011 03:27 PM

A,B,C,D are feeds coming in from power supply or feeding out to house???

Duck Butter 07-25-2011 03:39 PM

Quote:

Originally Posted by eman (Post 293271)
A,B,C,D are feeds coming in from power supply or feeding out to house???

feeds INTO the house. Had to change out the meter base before the electric company will bring power to us, thanks

eman 07-25-2011 03:54 PM

5=B = neutral
6=D= ground
4=A=line
3=c=line
w/ meter in place
6 will feed 5 neutral
4 will feed 2 line
3 will feed 1 line
I DO NOT SEE A GROUND BUS IN THE METER PAN.
IT MUST HAVE ONE!!!!

Country Boy 07-25-2011 03:54 PM

call me , i sent you a pm.

Shawn Braquet 07-25-2011 04:02 PM

Quote:

Originally Posted by eman (Post 293281)
5=B = neutral
6=D= ground
4=A=line
3=c=line
w/ meter in place
6 will feed 5 neutral
4 will feed 2 line
3 will feed 1 line
I DO NOT SEE A GROUND BUS IN THE METER PAN.
IT MUST HAVE ONE!!!!

6 is for the neutral from power company, small lug to the right of 6 is for the ground, 5 is for the neutral to the house, shouldnt need a ground bus as long as you land(bond) the ground on the small mechanical lug to the right of 6

Shawn Braquet 07-25-2011 04:04 PM

and 1 and 2 would be for power company as well with 3 and 4 feeding your house....this is how I would do it.

Duck Butter 07-25-2011 04:07 PM

Thanks for the help, got it figured now. The base has been out there for a year and just got around to getting the shed built, they wanted us to upgrade meter boxes. Thanks agai

Country Boy 07-25-2011 04:07 PM

give me a call if you need anything else but you should be good to go.

eman 07-25-2011 04:09 PM

Quote:

Originally Posted by Shawn Braquet (Post 293284)
6 is for the neutral from power company, small lug to the right of 6 is for the ground, 5 is for the neutral to the house, shouldnt need a ground bus as long as you land(bond) the ground on the small mechanical lug to the right of 6

I totally mised the ground lug bomded to the neutral bar .
I'll blame it on the glare spot and not my eyesight

Shawn Braquet 07-25-2011 04:27 PM

2/0 wire also, rated for 195 amps but the inspectors let that slide for residential, commercial they make us use 3/0